Flash and bang turning granny charger off

Flash and bang turning granny charger off

Author
Discussion

James6112

4,473 posts

29 months

Thursday 2nd May
quotequote all
agent006 said:
quinny100 said:
Pica-Pica said:
I would invest in a RCD adaptor for the charger as well.
Why would you do that?
Maybe you could explain why it's not necessary, because that's clearly what you mean.
The Op has RCD

Are you a qualified electrician, care to explain the benefit of 2 RCDs?

Edited by James6112 on Thursday 2nd May 23:47

quinny100

930 posts

187 months

Thursday 2nd May
quotequote all
OutInTheShed said:
quinny100 said:
The OP said the circuit in question is RCD protected.

Adding a second RCD is pointless because you have no control of which of the two RCD's will trip. It's not a case of the RCD nearest the load will trip, it's whichever reacts fastest. It adds no additional protection.

In this case where a relatively high current device is being connected to a socket you want to minimise the number of connections in the circuit. Suggesting a plug in RCD is just adding two more connections, two more opportunities for a high resistance connection which will generate heat and melt something.

The safest way to use a granny charger is to plug it directly in to a decent quality socket. Stopping the charge on the car is a good idea as it will remove the load on the socket switch when you turn it off.
I don't disagree, but the flip side is, break the circuit with a £15 plug in RCD, worst case, you lose £15 instead of calling out a sparky to change your socket.

This is a problem that should not happen, but I'm not knocked over by the surprise of it.
The safest and most cost effective resolution is to buy a new socket front for a fiver and fit it yourself. Changing accessories is not notifiable under Part P, so there is no legislative reason you can’t do the work yourself. You should only do so if you’re competent, of course.

TheDeuce

21,929 posts

67 months

Friday 3rd May
quotequote all
quinny100 said:
OutInTheShed said:
quinny100 said:
The OP said the circuit in question is RCD protected.

Adding a second RCD is pointless because you have no control of which of the two RCD's will trip. It's not a case of the RCD nearest the load will trip, it's whichever reacts fastest. It adds no additional protection.

In this case where a relatively high current device is being connected to a socket you want to minimise the number of connections in the circuit. Suggesting a plug in RCD is just adding two more connections, two more opportunities for a high resistance connection which will generate heat and melt something.

The safest way to use a granny charger is to plug it directly in to a decent quality socket. Stopping the charge on the car is a good idea as it will remove the load on the socket switch when you turn it off.
I don't disagree, but the flip side is, break the circuit with a £15 plug in RCD, worst case, you lose £15 instead of calling out a sparky to change your socket.

This is a problem that should not happen, but I'm not knocked over by the surprise of it.
The safest and most cost effective resolution is to buy a new socket front for a fiver and fit it yourself. Changing accessories is not notifiable under Part P, so there is no legislative reason you can’t do the work yourself. You should only do so if you’re competent, of course.
As per my post. Swap the socket front - if it flashed when the load was disconnected there was clearly a significant arc and some flyback voltage. Just swap it out.

Multiple RCD's on a circuit is pointless and not recommended.

To prevent the same happening again don't hard switch off a high current continuous load at the switch. Pull the plug on the car and the internal protection in the charger will deal with it = no arcing when you disconnect at the socket.

None of this is EV stuff...

Ardennes92

611 posts

81 months

Saturday 4th May
quotequote all
blank said:
Unlock the car and unplug the cable first.

Then when you switch it off it's not under load.
Definitely this, slowly, it is designed to be disconnected, potentially under load; not sure the switched socket was expected to be operated at 10A.

Discombobulate

4,867 posts

187 months

Saturday 4th May
quotequote all
blank said:
Unlock the car and unplug the cable first.

Then when you switch it off it's not under load.
This.

OutInTheShed

7,821 posts

27 months

Saturday 4th May
quotequote all
TheDeuce said:
As per my post. Swap the socket front - if it flashed when the load was disconnected there was clearly a significant arc and some flyback voltage. Just swap it out.

Multiple RCD's on a circuit is pointless and not recommended.

To prevent the same happening again don't hard switch off a high current continuous load at the switch. Pull the plug on the car and the internal protection in the charger will deal with it = no arcing when you disconnect at the socket.

None of this is EV stuff...
The socket needs swapping because it's soiled goods now.

The idea of using a plug in RCCB is that they are (or should be) capable of breaking a very high current without damage.
So ifi it's not convenient to soft switch off by going out to the car, you can just press the 'Test' button and the breaker will break.

Swapping out a mains socket is not a job for every DIYer. A sparks will charge £50 or more, you don't want to be doing that more than once.

The socket should be capable of breaking a 13A current. Maybe the socket's switch was compromised to start with?
Possibly the car plus granny lead presents a complex inductive load which gives the switch a hard time when breaking at full power?
Most high current domestic loads are simple resistive things like heaters. It's not unknown for switching off high power motors (e.g. garden shredder) to take out socket switches.

If switching it with a £15 RCCB kills the RCCB, you know you need to stop the charge at the car, and that knowledge has only cost you £15.

Anastie

Original Poster:

155 posts

159 months

Saturday 4th May
quotequote all
Thanks again all. The socket is going to be changed and I will in the future unplug from the car first.

I’ve chased my charge point with octopus to no avail as they won’t give me a date yet.